jlima1
Joined: 14 Feb 2008
Posts: 4
|
| Posted: Sat Feb 16, 2008 8:37 pm Post subject: GE NX-8V2 Control Panel - Service |
|
|
I just finished wiring my GE Alarm System. The service light is on and the fire light is flashing on the LED Keypad. The LCD keys are lite but the LCD is blank. I dont have a fire alarm connected. I cannot find anything in the instruction manual referencing this error. I checked my connections and everything looks good. I tried it with all the zones disconnected and still get the same lights. What should I do next?
Thanks,
Joe |
|
| Back to top |
|
Ian
Joined: 16 Dec 2005
Posts: 62
Location: Smithtown, NY
|
| Posted: Mon Feb 18, 2008 11:34 am Post subject: |
|
|
| Did you wire in all of you end of line resistors? They must be installed on all zones for the system to work. |
|
| Back to top |
|
jlima1
Joined: 14 Feb 2008
Posts: 4
|
| Posted: Tue May 06, 2008 7:16 pm Post subject: |
|
|
| Yes I put 3.3k resistors on one end of all ends of all the zones, including the motion sensors. I did not put a resistor on the two (1-LED& 1-LCD) keypads and the "bell" alarm circuits. |
|
| Back to top |
|
Ian
Joined: 16 Dec 2005
Posts: 62
Location: Smithtown, NY
|
| Posted: Wed May 07, 2008 10:06 am Post subject: |
|
|
Hello,
The bell circuit is supervised as well so you would need to put a resistor on that on as well. |
|